Design Master Wish List
Welcome to the Design Master Wish List, where you can submit your ideas for improvements to the software.
191 results found
-
Set number of spare breakers
Add an option to require a set number of spare breakers on every panel. The other breakers in the panel would be listed as spaces.
11 votes -
Select automatic conduit based on Type
When selecting conduit I want to be able to select the feeder as schedule 80 so that the only size option would be based on schedule 80. Then on another feeder I could select EMT for my circuits and the only option for auto sizing would be based on EMT. Finally, I would then have the option of adding the type to my one-lines and a conduit schedule.
11 votes -
Change Voltage of Project
Be able to change voltage of a completed project for 208V to 240V and keep everything connected and circuited.
10 votes -
Keep Tick Marks on Broken Circuits
When a circuit is broken, keep tick marks inserted on one of the halves.
10 votes -
Export the luminaire schedule into excel
I have lighting reps ask me all the time for an excel spreadsheet of our luminaire schedule. It would be helpful to export our luminaire schedule into excel.
9 votes -
Load Type Schedule Designation
Add a distribution schedule customization attribute that can be added to panel schedules as an additional column to show load type(s) that are connected to each circuit, preferably letter abbreviation designations for each load type. (Heating would be 'H', Lighting would be 'L', Motor loads 'M' etc...)
8 votes -
Customization of circuiting callouts
In circuiting callouts, allow the dash to be replaced by a custom string.
Example: Default circuiting callout is L1A-1,3,5. Allow us to make it say L1A: 1,3,5 or L1A CKT 1,3,5.
8 votes -
Support Paralleled Generators Connected to Switchboard
DM does not currently support more than one source on the Normal side of an ATS or the EM side of ATS, however larger I-2, I-3 occupancies generally have paralleled generators connected to a switchboard. This feature would avoid cumbersome work arounds.
8 votes -
Total Load in Project
Please add capability to total loads for the project before the circuiting is complete.
I would like to have a load sheet that keeps track of the total project load.
What I use now is a modified panel shedule that only shows the loads for a dummy panel I create called service. I connect all the panels together and then to Service. This gives me a total load analysis for the project, but only after the design is complete. I need to be able to confirm my loads and service sizing at the design development stage before circuiting.
A consideration…
8 votes -
Multi text search
implement Multi-Text search through out the menus.
So for example when searching through the Insert Receptacle menu and in my case we have several thousand pieces of equipment. if the equipment is called 'RX99S' instead of just allowing us to hit 'R' and starting us off at the beginning of the list of 'R' equipment allow us to type out 'RX99S' and design master go straight to the piece of equipment. this is a very simple change to the code in design master and would save tons of time on projects.
7 votes -
Add horsepower of individual loads on mcc schedules
The MCC schedule doesn't have the ability to show horsepower values for the individual loads. This is important information for the MCC vendor for breaker and overload sizing.
7 votes -
Demolition Layer Devices
I do not feel that the schedules should show counts for devices like receptacles and computer outlets that are on a demolition layer.
7 votes -
One-Line Distribution Equipment "Wrapping". For printability
Often times MCC's have so many loads on them that once they are generated as a One-Line, they are too long and can no longer be printed without truncating off most of the loads for printing.
The current recommended solution is to divide the loads into MCC sections and then to connect them as sub-feeds to the parent MCC. This solution is convoluted and not easily scalable. True support of this fundamental need is requested.
I request a dedicated wrapping functionality that allows the user to select where on distribution equipment the user would like for the distribution equipment to…
6 votes -
Voltage Drop Based upon Connected or Other Load
Be able to specify that the voltage drop on a feeder should be based upon the connected or other load, rather than the calculated load.
One example of a use for this feature is a piece of equipment that serves a single motor. You want the voltage drop for the connected load of the motor, rather than the calculate load, which will be 125% of the motor load.
6 votes -
Low-voltage looping
Be able to draw loops between devices for low-voltage lines, for connecting items like sensors and power packs.
6 votes -
Do "Amps by Phase" using calculated loads on high-leg delta panels
High-leg delta panels are always unbalanced. The balanced 3-phase amps we display is not a good number to use when sizing these panels. The connected amps by phase does not account for largest motor loads or continuous loads.
Add the ability to determine the amps by phase using calculated loads. The largest motor, lighting, and continuous loads would all be calculated at 125%. All other loads would be calculated at 100%.
6 votes -
Low Voltage Homerun With Keynote
On low voltage systems drawings (Fire Alarm, Security, CCTV) we treat homeruns differently than power and lighting homeruns. We do not use the circuit label, wire callout, or tick marks, but rather we use a keynote. If there was a “keynote homerun”, it would save us the time spent removing the wire call-out every time we create low voltage homerun.
6 votes -
Handle LED Lighting Better
Calculate the load based upon the length and the remote transformers.
6 votes -
Reset panel "Fixed Loads".
Often, I need to "start over" on a panel that I've assigned fixed loads. It would be handy to have a button that would clear every fixed load on the panel. Or even be able to select several circuits and clear those circuit's fixed loads.
5 votes -
Unique ID for all Feeders and Branch Circuits
Have a way to make a unique cable ID for every feeder, branch circuit and low voltage circuit. For example P-MCC1-001 for the power cable fed from MCC1 or PT-FLOWGAS-003 for a pressure transmitter.
I'm working on a big industrial plant where I need a have a cable number for every cable in the plant.
I would like to have the ID on the one line, plan view drawing and export to Excel.
5 votes
- Don't see your idea?